Post by Uncle Bob on Jun 13, 2011 17:23:40 GMT -6
Ok, senile old man has gone back to work; and, an inspector told me to write up a code violation for a hip ridge rafter? board?; being too long without bracing. My answer was " I am not sure there is a violation. Can you give me a code section?"
1. Is it a hip ridge rafter; or hip ridge board?
2. I understand purlin bracing for rafter spans; but, I do not remember bracing requirements for hip ridges; accept in the case where a splice is required to accomodate the length of the ridge; and there has to be a support under the splice; and, two boards are needed because the length is too long and they don't sell lumber that long or they used two short boards; and a splice is required to accomodate the length of the ridge; and there has to be a support under the splice.
I did ask for a code reference; answer "It just don't look right to me; I want a purlin brace there".
I also understand rafter spans. Anyone have a code reference limiting hip ridge spans without bracing? Take your pick of IRC's; I'll find it ( I got'em all ) ;D
have I been gone too long?
Uncle Bob
|
|
|
Post by purplegolf on Jun 14, 2011 13:34:44 GMT -6
The only thing I see is in IRC 2006 802.3, which states that "Hip and valley rafters shall be supported at the ridge by a brace to a bearing partition or be designed to carry and distribute the specific load at that point". I don't know if this is exactly what you are talking about.
|
|
|
Post by kzq on Jun 14, 2011 14:15:45 GMT -6
Hi Bob,
Sec R802.3 (2009) calls it a Hip Rafter. Which as purplegolf says must be supported at the ridge by a brace to a bearing partition. I did find one hint in the last sentence of that section where it requires ridges, hips and valleys to be designed as beams when the roof pitch is less than 3/12.
This would lead me to the conclusion that there is no length limitation to a hip member.
This is troubling to me however because I know that valley members need support and this is not addressed at all.
Bill
|
|
|
Post by Uncle Bob on Jun 14, 2011 17:02:25 GMT -6
Thanks Ya'll,
I agree; there is no minimum span; as there are for rafters, where a purlin brace would be required for over spaned rafters. I just don't write anything I can't back up with a code reference. I was taken by surprise when the other inspector insisted on requiring a brace half-way down the hip.
Thanks again,